CyberPower OL1000RTXL2U Smart App Online UPS System

CyberPower OL1000RTXL2U Smart App Online UPS System

Good job woot, not including the one number (watt hours) that matters, in the spec sheet. /eyeroll

Woot only posts what is provided to them. Most UPS manufacturers state the battery capacity in Volt Amps (VA) not Watt Hours (WH).

Here’s the info from the manufacturer.

Nowhere do they provide the Wh capacity.

2 Likes

I couldn’t just leave it there.

In the specs:
Runtime at Full Load - 7.4 min
Runtime at Half Load - 20 min

Assuming “full load” is 900W

7.4 minutes is 0.123h
20 minutes is 0.33h

900w * 0.123h = 110.7Wh (approx)
450w * 0.33h = 148.5Wh (approx)

This is due to how lead acid batteries and inverters behave under different loads and I believe is part of the reason UPS manufacturers state capacities in VA and not WH. Someone smarter than me could probably explain it better.